yes, the modules isn't new, and has been assigned F-address before, could you tell me how to refactory it or solve it? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 09/09/2021 13:59:04New subject after splitting |
|
8/30/2021 8:38 AM | |
Joined: 3/11/2019 Last visit: 9/6/2024 Posts: 1569 Rating: (287) |
Hi, the module diagnostics says "F-Adress memory not accessible". Please check, if the memory (coding element) is plugged in.... the coding element is needed to store/save the safety-parameters on. The coding element can be found between module and baseunit of ET200SP modules. Please check the following links, there are also pictures for the coding element. What should you check when the F destination addresses cannot be assigned?regards sancruz |