Dear hefeng_05, if you want to access the input-channels of the DI, you have to use the adress I x.0 - I x.3 (or I x.7, if you use 1oo1) for the DO-module, you have to use Q x.0 - Q x.3. The rest of the adress range is used for the PROFIsafe protocoll. For details have a look at chapter 3 in the manual 'S7 F - ET 200S, Fail-Safe Modules' Best regards, yy1 |