Good evening, I don't want to start a new topic so I'll put my problem description here: Via Tia V18 or by the memory card I received the same message: ------------------------------------------------------------------------------------------ |
Last edited by: thirsty_krusty at: 01/24/2024 21:23:21Last edited by: thirsty_krusty at: 01/24/2024 21:27:46Last edited by: thirsty_krusty at: 01/24/2024 21:28:03Last edited by: The Helping Hand at: 01/25/2024 07:29:08New subject after splitting |
|
1/24/2024 9:43 PM | |
Joined: 7/7/2010 Last visit: 12/11/2024 Posts: 15491 Rating: (2456)
|
Look in the Diagnostics, especially the Diagnostics -> Diagnostics buffer as shown in your "Online access" working pane in the uploaded image. Find out what is wrong with the PLC first. Then power cycle the PLC. Once the PLC is in a happy state, try the Online access firmware update again. It is possible your downloaded firmware is named correctly, but not downloaded correctly. Let's say your mouse was shaking a little the day the file was downloaded, and the name was forced to be the expected filename rather than accepting what it was trying to call itself. I've accidentally done the same thing myself which is why I suggest it as a possible cause.
|