1/20/2012 1:24 AM | |
Joined: 9/27/2006 Last visit: 9/25/2024 Posts: 12282 Rating: (2685) |
Hello D; I am just curious, but yourdescription would seem not to require a failsafe module, but a hazadous zone (Ex)module (for explosive areas). Just to examine the possibilty, maybe you could look at the following manual; it shows how these Ex modules for S7-300 and ET200M can be connected to TCs and RTDs, and what certifications they are covered by. SIMATIC Automation systems S7-300, ET 200M Ex I/O Modules The SIMATIC S7 Ex modules have the following FM licenses: • Class I, Division 2, Group A, B, C, D Tx; • Class I, Zone 2, Group IIC Tx Therefore, the modules can be used in areas that contain volatile flammable liquids or flammable gasses which are normally within closed vessels or systems, from which they can only escape under abnormal operating or fault conditions. The license applies to all test gasses. A surface temperature no greater than 135 °C (T4) occurs at ambient temperatures of 60 °C. Hope this helps, Daniel Chartier |
1/20/2012 3:48 PM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308) |
Hellodshha, Unfortunately Siemens doesn't have a SIL2/3 module that supports RTD/TC directly. You have said that you require an isolated safety barrier. So, you should buy a SIL2 intrinsically safe signal converter like thisoneof P+F. If you require redundant I/O (sometimes in SIL2) then you should buy something similar to thisone. In both cases ET200iSP F-module won't be of much benefit and ET200M F-module will be good. I'm sure you can find the same in MTL or TURCK or Weidmuller. Best regards. H-H
|
This contribution was helpful to2 thankful Users |
1/31/2012 8:08 AM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308) |
Deardshha, I'm really sorry for my late reply. Yes you have to use SIL2 I/O modules Yes, Everything should be SIL2 even transmitters and actuators have to be SIL certified. Best regards. H-H
|