1/8/2015 10:11 AM | |
Posts: 8 Rating: (0) |
thanks again my questions may seems stupid, but how to check r949 and r947, i reached them then i push EN, i get r00000 for both, is that correct?
|
1/8/2015 11:07 AM | |
Joined: 10/11/2006 Last visit: 4/26/2024 Posts: 5825 Rating: (789)
|
I assume you are trying to check the values with the BOP. At first you have to check that youare on the right drive object where the fault occurs (the number of the drive object can be seen on the upper left part of the BOP, 01 is the CU, 02 is the first axis/infeed etc.) Change the Drive Object number to thecorrect drive by pressing together FNand the arrow up buttons. If you are at the right Drive Object then checkat which index in r947 the F30611 can be seen. For that go to parameter r947 and check all indexes (you see In0000 for Index 0 etc.). The fault value for F30611 will be then seen exactly at the same index in r949. E. g. F30611 can be seen in r947[2] then r949[2] will show the fault value for F30611. Operation description for the BOP can be found here: http://support.automation.siemens.com/WW/view/en/99687313 However it would be much easier to go Online with Starter/Scout and check the fault window. |
With best regards, |
|
1/9/2015 9:49 AM | |
Posts: 8 Rating: (0) |
All i succeed to have is 8010 at 947 949 i get in0 to 63 and all seems to have 0 value
|
1/9/2015 12:05 PM | |
Posts: 8 Rating: (0) |
thanks for your help |