8/16/2006 9:41 PM | |
Posts: 21 Rating:
Is it possible to determine in the program if a CPU is in fault mode and write a function, for example, to activate a digital output? |
8/17/2006 9:28 PM | |
Joined: 1/7/2006 Last visit: 7/3/2023 Posts: 2705 Rating:
Hi Donflore, With Report System Error you can find all system errors, the mandatory FB49, DB49 are called in all OB8x and are giving the right information for the errors. When you use STEP7 then the errors are as events put to STEP7 (very nice if you are testing the installation to check everything).[:o] Configuration of "Report system errors" and display in STEP 7 V5.1for STEP7 V5.4 it is not the same but you will find the way to do it. The organisationblocks for the errors having incoming and outcoing events, in the 20 byte that are in the header you can filter out what happened, with help <F1> on the OB8x the 20 bytes are described... [;)] |
8/19/2006 2:31 PM | |
Posts: 21 Rating:
Thanks for the tips ... |
