12/28/2019 8:09 AM | |
Joined: 8/24/2006 Last visit: 4/3/2023 Posts: 148 Rating:
|
Hi at all, FB219 (ack) must be ONLY ONCE in safety program an the end: please can you confirm??? Thank you!!! |
12/28/2019 6:47 PM | |
Joined: 9/27/2006 Last visit: 5/27/2023 Posts: 12022 Rating:
|
Hello dstudio; You are almost correct: FB 219 is allowed only once per F-runtime group in a Distributed Safety program. See the screenshot below, extracted from the Distributed Safety configuring and programming manual: SIMATIC Industrial Software S7 Distributed Safety - configuring and programming https://support.industry.siemens.com/cs/us/en/view/22099875 Hope this helps, Daniel Chartier |
12/28/2019 7:02 PM | |
Joined: 8/24/2006 Last visit: 4/3/2023 Posts: 148 Rating:
|
So only one time in any part of sw. Thank you. |