Hi Jey@tokyo, As far as I know you cannot communicate safe data between the 400H CPUs and S7300F CPUs using the method you describe. Please see the section 8.8 of the S7DistSafety manual. You will need a 300F Profinet version and must use Ethernet with S7 connections. Please read the getting started manual for S7 Distributed Safety see attached. The safety blocks must be called within an F-FC or F-FB which you create. You can create an FFB/FFC in the same way as a standard block except you must choose the F-LAD or F-FBD language instead of LAD/FBD. Call FRCV-S7 at the beginning of the program and FSEND-S7 at the end. In the blocks folder insert an FC and use the language called FCall instead of FLAD/FFBD. Double click the FCALL block and assign your program to the FCALL. You then need to call the FCALL in either a cyclic OB or OB1. Attachments7fcoGSb.pdf (1159 Downloads) |