11/7/2017 1:12 PM | |
Posts: 17 Rating:
|
Dear hulz The alarm on the PLC is external fault. |
11/7/2017 2:28 PM | |
Joined: 9/27/2006 Last visit: 3/26/2025 Posts: 12344 Rating:
|
Hello frank; There is an excellent tool on S7 PLCs called the diagnostic buffer, where the CPU's operating system logs messages when it discovers issues that affect the PLC operations. I believe that this was what Sabine was asking about in her earlier post. If you have access to the programming software for your PLC, go online and open the diagnostic buffer ot see what messages you can find relating to a Profinet connection problem with your drive. Save the buffer and post it here (there is a button on the buffer page to save the file in .txt format) and attach it here if you have trouble understanding the messages. Now, we can try looking at diagnostics form another source: here is some information from Danfoss and Danfoss users on the Fieldbus error W34: Troubleshooting FC Programming GuideLook at page 212, extract as attachment below. This seems to indicate that the Profinet interface card on the drive is not installed or parameterized properly. Maybe the links below can provide a bit of information; if not, you should contact Danfoss directly. Danfoss Warning 34 Fieldbus Fault — InControl IM151-8 Bus Fault when using Danfoss FC302 and Profinet faulty profibus net with danfoss fc302 - PLCS.net Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 11/7/2017 2:29:55 PMLast edited by: dchartier at: 11/8/2017 2:32:44 PM |
|
This contribution was helpful to
2 thankful Users |
11/9/2017 8:18 PM | |
Joined: 9/27/2006 Last visit: 3/26/2025 Posts: 12344 Rating:
|
Hello frank; That is quite normal behavior. Grounding Profius cables protects the bus from EMC (electromagnetic compatibilty) and interference voltage issues. Removing the ground connection can cause a lodss of signal transmission to the node. See the extract below, from the first link in the following suggestions: PROFIBUS Network Manual - Industry Support Siemens A short guide to addressing EMC on PROFIBUS - Procentec PROFIBUS Installation Guideline for Cabling and ... - Profibus Centre Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |
11/10/2017 11:53 AM | |
Posts: 17 Rating:
|
Hi Daniel, Should I need to connect the profibus shield to the main grounding of the control room before disconnecting it on the VFD? Thank you. |
11/11/2017 7:40 AM | |
Posts: 17 Rating:
|
Hi Daniel, Is there any software used to analyse the status of Danfoss VFD? Your immediate response is highly appreciated. |