8/4/2014 9:51 AM | |
Joined: 4/22/2010 Last visit: 1/15/2025 Posts: 5697 Rating:
|
Hello, Cpu's with firmware 1.0 can't be updated to V3, i think 2.2 is the highest version. you will find the updates Here, look for the right partnumber and click the link for a short description how to perform a update and the firmware . Regards, Marcjan |
Problem solved? |
|
This contribution was helpful to
2 thankful Users |
8/4/2014 11:18 AM | |
Joined: 10/20/2011 Last visit: 12/12/2024 Posts: 102 Rating:
|
Dear sir, Thank you for your kind reply.you r correct.Please send me the procedure expect using MMC or web server.
|
8/6/2014 6:09 AM | |
Joined: 10/20/2011 Last visit: 12/12/2024 Posts: 102 Rating:
|
Dear sir, Please send any other procedure to upgrade Firmware Without using MMC. |
8/6/2014 7:18 AM | |
Joined: 4/22/2010 Last visit: 1/15/2025 Posts: 5697 Rating:
|
Hello, The only other way to update firmware is through a webserver, that is only possible as from firmware version 3. How do you perform a firmware update for the S7-1200 as from V3.0 in STEP 7 (TIA Portal) by means of the web server? Regards, Marcjan |
Problem solved? |
|
8/6/2014 8:43 AM | |
Joined: 10/20/2011 Last visit: 12/12/2024 Posts: 102 Rating:
|
Dear sir, Can able to use 12MB memory card for Firmware upgradation ? |
8/6/2014 8:57 AM | |
Joined: 4/22/2010 Last visit: 1/15/2025 Posts: 5697 Rating:
|
Hello, I don't think so because
What CPU do you have there? Please give us the full partnumber(6ES7 xxxx). Regards, Marcjan |
Problem solved? |
|
8/6/2014 9:13 AM | |
Joined: 10/20/2011 Last visit: 12/12/2024 Posts: 102 Rating:
|
Dear sir, CPU - 6ES7 214-1AE30-0XB0 (1214C DC/DC/DC) Version - 1.0
|
8/6/2014 3:01 PM | |
Joined: 7/7/2010 Last visit: 1/17/2025 Posts: 15541 Rating:
|
Using the right MMC Version 1.0 can be updated to Version 2.2. To get to version 3.0, you need a new PLC - different part #. The latest is version 4.0, and yes, it is also a different part #. |
science guy |
|