Hello, First of all, the first sentences of the entry about V2.1 tells you that you can use your current STEP7. See here: http://support.automation.siemens.com/WW/view/en/32599720 Secondly, because it is a CP, you must use the FW loader of NCM. The procedure is described here: http://support.automation.siemens.com/WW/view/en/12213669 |
Best regards |
|