4/9/2010 3:57 PM | |
Joined: 8/10/2009 Last visit: 7/10/2022 Posts: 29 Rating: (2) |
This error is an absolute encoder frame error. The baud rate of the encoder transfer may be too high for the length of cable, simply reduce this frequency in parameters and see if the problem is eliminated. It could also be a bad cable or bad encoder. To verify this, you would need to check the signal integrity of each signal with an oscope. You can find the pinout for the encoder cablein the CAM module manual in appendix B. I have attached this manual. AttachmentS7FM352b.pdf (73 Downloads) |