sir how to use fm module (FM6ES7 350 2AH01 0AE0) IN H SYSTEM(6ES7 4HM14 0AB0) |
8/29/2012 7:13 PM | |
Joined: 9/27/2006 Last visit: 9/13/2024 Posts: 12282 Rating: (2683)
|
Hello ahmad; The reason you will find no specific application for the programming of the FM 350-2 in a S7-400H environment is simply because it is the same programming as for any other Siemens S7 CPU. The attachment shows the FMs and CPs supported by H-systems in a "distributed switched use", that is as part of a redundant ET 200M (2x IM 153-2 with active bus modules). This was taken from Appendix D of the following manual: SIMATIC Fault-tolerant systems S7-400H Information on the ET 200M-red bundle can be located here: http://support.automation.siemens.com/WW/view/en/28199808 and you will also need an active bus module for all modules on the redundant ET 200M: http://support.automation.siemens.com/WW/view/en/15346950/133200 Once the hardware is installed correctly in the redundant ET 200M, including the FM 350-2, you simply configure it as a slave to both redundant cPUs, and create a single program that will be downloaded to both the primary and standby CPUs of the S7-400H system. You can use the sample program you already have as a basis for your own program. Hoppe this helps, Daniel Chartier |
Last edited by: dchartier at: 8/30/2012 1:26 AM |
|