12/27/2008 7:47 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (306) |
Hello, First of all, be sure that you have the latest configuartion software for the FM. Here you will find it: http://support.automation.siemens.com/WW/view/en/28309520 Setup this software. 1) create a project with your FM In that project insert the FC0, FB1, FB2 that you find in the library installed with the setup. Also copy the correct UDT that will contain the parameter assignments. You have 32 tracks max per module, and the module provides up to max.128 cams, which can be assigned to any track. If you use 128 Cams, you will have to use also the CAM_P128TYPE (UDT6), and create a DB with UDT6. 2) In the HWconfig, once you have placed an FM352 in the rack, by double-click on the module, the configurator opens.In the menu "file" of the configurator, you can choose "import", and open the DB you have created. By clicking on the cams symbol, you open the cam configuration. You make now all settings required (activating, assigning to a track, ...), and you export back to the DB.. 3) After the setup of the software, an example is also installed in the S7 Manager. If you go to the menue File ==> open, select now the tab "sample projects", and select zEn19_02_FMx52___Prog You will find 5 folders with sample programs. These are the examples described in the manual in chapter 13. Link to the manual: http://support.automation.siemens.com/WW/view/en/2103044 You can adapt the example to your needs. |
Best regards |
|