4/10/2012 1:59 PM | |
Joined: 4/22/2010 Last visit: 2/26/2025 Posts: 5697 Rating:
|
Hello, You need to build in a hysteresis, can be done like in attachment (step7 5.5) Or use a pid. Regards, Marcjan AttachmentFC2.pdf (625 Downloads) |
Problem solved? |
|
4/11/2012 7:49 AM | |
Posts: 23 Rating:
|
Thank you! I think that the right thing to do is to use PID compact. Can someone guide me through the cofiguration or lead me to some manual? |
4/11/2012 8:24 AM | |
Joined: 3/21/2006 Last visit: 3/19/2025 Posts: 10239 Rating:
|
AIO: Share Samples and Tips Application for PLC S7-1200 & TIA PORTALBest regards, Hristo Mihalev
|
4/11/2012 8:44 AM | |
Posts: 23 Rating:
|
Thanks! Is there a difference between v10 and v11? Because I found it explained for v10.
|
4/11/2012 12:38 PM | |
Joined: 3/21/2006 Last visit: 3/19/2025 Posts: 10239 Rating:
|
The only difference there (V11) isPID goes ininactive mode after every restart of the PLC. (Kindly provide v11 project and libraries for PID). But have possibilities to receive an errors durring migration...too.(S7-Basic V11 conversion problem). best regards, Hristo Mihalev |
Last edited by: UMENCHO at: 4/11/2012 12:39 PMtypo |
|