Dear All, Can any body help me for below conditions I am using G-120 Drive PM240-E2 Condition 1: DI0=1 & DI2=0 Then Motor should run on 50Hz in forward direction. DI1=1 & DI2=0 Then Motor should run on 50Hz in Reverse direction. Condition 2: DI0=1 & DI2=1 Then Motor should run on 25Hz in forward direction. DI1=1 & DI2=1 Then Motor should run on 25Hz in reverse direction. ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 12/29/2018 2:08:07 PMNew subject after splitting |
|
12/31/2018 3:45 PM | |
Joined: 2/7/2015 Last visit: 2/11/2025 Posts: 33 Rating:
|
Hello M.S.Saloji This is simple task that you can run on the sinamics drive : You can use fix frequency function . 1-assign DI0,DI1 and DI2 to the inputs. assign DIx to p1020[x] 2- put p1001= 50 HZ (you should put the rpm !!!) put p1002= - 50 HZ (you should put the rpm !!!) put p1003= 25HZ (you should put the rpm !!!) put p1004= - 25 HZ (you should put the rpm !!!) |