8/28/2015 5:24 PM | |
Posts: 305 Rating:
|
.... |
8/28/2015 5:59 PM | |
Joined: 5/12/2006 Last visit: 4/17/2025 Posts: 22597 Rating:
|
Hello, G120 doesn't support IRT Communication.
|
8/29/2015 2:42 PM | |
Posts: 305 Rating:
|
G120C and simotion via PN,master is SIMOTION ,it control G120C speed of run ,witch mode can di it ?what is the command? |
8/31/2015 2:31 AM | |
Posts: 305 Rating:
|
at the same BUS, has S110 (by IRT ),G120C (by RT),is it have any problem ? S110 to do sever control ( e.g. ptp ),G120C to do speed control ! |
9/1/2015 1:13 AM | |
Posts: 1529 Rating:
|
Your controller and S110 need to be in an IRT domain ( and connected sequentially). You can mix IRT and RT with no problem. |
9/1/2015 3:02 AM | |
Posts: 305 Rating:
|
thanks . i need to do it . s110 by IRT ,G120C by RT .
|