7/9/2022 1:31 AM | |
Joined: 9/10/2014 Last visit: 10/31/2023 Posts: 21 Rating:
|
I found the solution. 2) Download the file "82843076_SINAMICS_G_Drives_V2.0.zip (11,4 MB)" 3) Unzip the downoaded file 4) Install the "Siemens G Drive - T999.eds" into your PLC engineering software 5) Configure IP address and Subnet mask 6) In Starter or Startdrive, configure the IP address, Subnet mask, gateway, adjust the field bus protocol (P2030) for EtherNet/IP [10], keep the EtherNet/Ip profile (P8980) adjusted to SINAMICS [0], then adjust Telegram configuration (P922) to "Free telegram configuration with BICO [999] 7) The last and not less important, the PZD maximum interconnected (r2067[0] and r2067[1]) should show the values: r2067[0]=12, r2067[1]=17. If the r2067[0/1] have different values, then go to the "Communication\Field bus" menu and define each word into "Receive direction" and "Transmit direction", after these definitions, the r2067[0/1] will show 12 and 17 as actual values. 8) Copy RAM to ROM 9) Power off the drive 10) Power on the drive 11) It's done! Regards, Thiago Penezi |
This contribution was helpful to
2 thankful Users |
11/3/2023 10:25 AM | |
Joined: 1/8/2020 Last visit: 11/29/2023 Posts: 1 Rating:
|
Can you in some way share the file? it is not more aviable and i need to comunicate to Rockwell PLC. Thankyou
|
11/8/2023 8:16 AM | |
Joined: 6/19/2017 Last visit: 12/7/2023 Posts: 7572 Rating:
|
Hello AleBaz76, please use following link: https://support.industry.siemens.com/cs/ww/en/view/109824950 Best regards, |