1/23/2016 9:02 PM | |
Posts: 111 Rating:
|
I am configuring G120 drive and it is giving me fault of "1910: Fieldbus interface setpoint timeout " and when I am clicking the green arrow in the control panel above the fault code it is bringing me to this page but when I am trying to find out parameter P1170 in parameter list it's not there. Can anybody help? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 1/25/2016 9:21:12 AMNew subject after splitting |
|
1/24/2016 6:55 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Please check value of p2040. It should not be = 0 |
This contribution was helpful to
1 thankful Users |
1/25/2016 3:26 PM | |
Posts: 111 Rating:
|
PISCEAN 2010! Should I change P2040 to 1? |
Last edited by: Shahjee at: 1/25/2016 5:50:43 PM |
|
Follow us on