3/16/2023 2:27 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, check encoder settings and reference value vor speed setpoint. Move with drive control panel and trace actual velocity and actual position at the TO. Fits the speed in the drive to the velocity at the TO? If not check configuration of encoder, If yes check reference value. 5.4 Configuring the positioning axis technology object Data exchange with the drive In this area, you can configure the scaling of the setpoint speed: ● Reference speed The reference speed of the drive is the speed, with which the drive spins when there is an output of 100% at the analog output. The reference speed must be configured in the drive, and transferred into the configuration of the technology object. The analog value that is output at 100% depends on the type of the analog output. As an example, for an analog output with ±10 V, the value 10 V is output at 100%. ● Maximum speed In this field, specify the maximum speed of the drive. The maximum speed is limited by the drive and by the value range of the analog output. In the simplest situation, the reference speed and maximum speed are identical. Analog outputs can be overloaded by approximately 17%. If the drive permits overloading, you can use this to operate an analog output as a limit in the -117% to 117% range. ● Invert drive direction To invert the rotation direction of the drive, select the check box. 5.4.3.3 Configuration - Encoder Encoder connection Depending on the selection of the encoder connection, you configure various parameters in the "Encoder" configuration window. The following encoder connections are possible: ● Encoder on high-speed counter (HSC) (Page 82) ● PROFIdrive encoder on PROFINET/PROFIBUS (encoder on drive, encoder on technology module, PROFIdrive encoder) (Page 79) 5.4.4 Extended parameters 5.4.4.1 Mechanics https://support.industry.siemens.com/cs/ww/en/view/109773400 |
With best regards, |
|
This contribution was helpful to1 thankful Users |
3/23/2023 7:19 PM | |
Joined: 7/2/2017 Last visit: 12/10/2023 Posts: 5 Rating: (0) |
Hello, thank you for you help, i figured out that my problem was in the encoder, it has a floating pin that should be connected to ground. every thing is working fine now, thanks again. Regards.
|