8/4/2008 9:55 AM | |
Posts: 739 Rating:
|
Ther is no possibility to feed the energy back into UPS!That means your G120 (PM250) will switch off with failure. For more technical consulting please contact the Technical Support for Automation & Drives SIEMENS AG Tel: +49 (0) 180 5050 222 Fax: +49 (0) 180 5050 223 Mail: adsupport@siemens.com |
8/13/2008 9:50 AM | |
Posts: 1 Rating:
|
... is it workable if we put one load, e.g resistor in parallel with PM250 input just to consume the regenerative power? |
9/19/2008 9:59 AM | |
Posts: 739 Rating:
|
... I’m afraid, it’s not possible. Therefore you have to use a PM240 |