Hello Autogen_6024931, Did you managed to solve the problem.? I have the same problem but with siemens own G120 drives which does not supports System redundancy S2. From the siemens documents it is not recommended to connect S1 devices to PCS7 Redundant system. Please suggest me any possible way i have to follow to get communication with G120 drives. Thankyou in advance. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/13/2023 08:23:53New subject after splitting |
|
11/8/2024 7:37 AM | |
Joined: 9/5/2012 Last visit: 11/18/2024 Posts: 12 Rating: (1) |
to connect G120 or G220 with S1 to a redundant system, you need a "Y-Switch". So called DNA Switch: 6GK5204-2AA00-2YF2 |