8/26/2020 8:04 AM | |
Posts: 4 Rating: (0) |
Sorry for the child's question. How to choose between CDS0, CDS1 and CDS2 using the digital inputs? |
8/26/2020 8:36 AM | |
Joined: 9/23/2005 Last visit: 1/15/2025 Posts: 4846 Rating: (741) |
If you want to play like this it's high time you read the book for big boys. This specific one might not match your CU. Find matching one then. Pages 589, 790. |
Regards, |
|
8/26/2020 8:46 AM | |
Posts: 4 Rating: (0) |
Jacek, I didn't mean to offend you ... |
Last edited by: KRAFT8 at: 08/26/2020 08:47:03 |
|
8/26/2020 11:49 AM | |
Joined: 10/11/2006 Last visit: 1/14/2025 Posts: 5982 Rating: (823)
|
Hello, yes you can use a digital input to change the CDS. You can find an application example which shows the parameter settings to use different CDS. https://support.industry.siemens.com/cs/ww/en/view/59193378 |
With best regards, |
|
8/26/2020 3:47 PM | |
Joined: 7/7/2010 Last visit: 1/14/2025 Posts: 15533 Rating: (2465) |
In my work, we do this with digital inputs when we do not need fast response from the drive. If we need it to switch quickly, we use BICO and a spare word in the telegram to activate the change. The profinet telegram updates much faster than digital I/O. Just something to think about if you know in advance the switching needs to happen more predictably, timely, quickly, & reliably (because digital I/O is more likely to fail than a telegram bit).
|