Need help for g120 p module and cu230p-bt When power turnd on led indecator flush red And we connect throw starter connect and get info And parameter when down load to drive get errore r7760 and dont reset to factory default Pls help ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 09/19/2023 07:36:29New subject after splitting |
|
9/19/2023 11:51 AM | |
Joined: 7/19/2022 Last visit: 2/12/2025 Posts: 434 Rating:
|
Hello AutoGen_5105717, Parameter r7760 indicates that you have write protection activated, which means that you cannot modify parameters or do a factory reset. To remove write protection you must set p7761=0 |