7/5/2021 5:01 PM | |
Joined: 5/30/2016 Last visit: 2/5/2024 Posts: 16 Rating: (0) |
Hi, G120C is connected to plc with Telegram 1. Even the inverter is not in fault, plc shows "error in lower-level component". When I go online with G120C, I don't see any faults. Seems like I can't configure inverter configuration. Can you please help me for solving the issue? Note: Checked Telegram 352 and the result is same. Inverter control is functioning well, just I have to resolve "lower-level component" fault. Attachmentss.zip (158 Downloads) |
7/6/2021 11:35 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (871) |
To start inverter 047F & then 047E bit 0 start command is edge controlled. |
7/6/2021 11:39 AM | |
Joined: 5/30/2016 Last visit: 2/5/2024 Posts: 16 Rating: (0) |
So is this exactly what I'm doing? Couldn't find where to fix |
7/6/2021 12:43 PM | |
Joined: 5/30/2016 Last visit: 2/5/2024 Posts: 16 Rating: (0) |
I forgot to add Scalance. When I add Scalance in topology, led gone to green and working fine. Thanks |