I have G120C 6SL3210-1KE23-8UF1 version BO3/ V 4.7 Problem is when ever main power recycle every time Speed set point I have to manually enter and start the drive from BOP. So need your support. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/29/2019 05:49:27New subject after splitting |
|
11/29/2019 10:39 AM | |
Joined: 10/11/2006 Last visit: 1/22/2025 Posts: 5985 Rating:
|
Hello, please check out chapter 6.2.7 “Automatic restart”, of the G120C operating instruction manual. https://support.industry.siemens.com/cs/ww/en/view/109757226 But using that you have to use a setpoint/command source other than the BOP, e.g. fixed speed setpoint. You can find more information regarding setpoint sources in chapter 6.16 of the G120C operating instruction manual. |