1/7/2020 11:37 AM | |
Joined: 10/11/2006 Last visit: 12/1/2023 Posts: 5716 Rating:
Hello, in your case I think that the only possibility is the jogging mode. Commands "Jog 1" or "Jog 2" switch the motor on and off automatically and as soon as the motor is on, the motor accelerates to the setpoint, jog 1 or setpoint, jog 2. The two different setpoints can, for example, be assigned to motor clockwise and counter-clockwise rotation. Parameter Description p1055 = 722.0 Jogging bit 0: Select jogging 1 via digital input 0 p1056 = 722.1 Jogging bit 1: Select jogging 2 via digital input 1 p1058[D] Jogging 1 speed setpoint p1059[D] Jogging 2 speed setpoint
Have a look at chapter 6.3.8 of the following manual: https://support.industry.siemens.com/cs/ww/en/view/109769350 |
With best regards, |
This contribution was helpful to
1 thankful Users |
Follow us on