Hello aliuta;
|
This contribution was helpful to3 thankful Users |
7/8/2011 3:46 AM | |
Joined: 9/27/2006 Last visit: 9/13/2024 Posts: 12282 Rating: (2683)
|
Hello aliuta; The foillowing attachment is taken from the S7-300 Module Data manual, a very important and useful document when dealing with S7-300 IOs. http://support.automation.siemens.com/WW/view/en/8859629 It shows a tablke for the temperature transmitted by a J-type TC, and the resuting value of the analog channel. TCs are an exception in analog reading rules, in the S7 world; look at all other similar tables in chapter 5 to see this. Notice that in the J-TC table for values in degrees C, the multiplier is exactly 10. If you are read a temperature of 200 C, the reading at your PIWxxx address will be 2000. Divide by 10 and you will have your exact temperature (as an integervalue, no decimal). Same applies for negative values. You do not need top scale using FC105 for TC readings. Test it yourself, it should pose little problem. Hope this helps, Daniel Chartier |
7/25/2011 9:38 AM | |
Joined: 1/26/2007 Last visit: 8/27/2024 Posts: 123 Rating: (4) |
of i divide by 10 i gat a non relaistic valaue . for Ex now is about 25 degree outside in the enviremonet , and if i divide by 10 the value of piw i get 53.8 degree C .... or i shoud divide by 10 before get the real value from the PIWxxx??? Thanks a lot |