9/22/2016 7:39 AM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (927) |
Hi guys, Can't find the exact answer I need... I have a S7400 CPU which should communicate with a S71500. Communication is done through Industrial Ethernet via Get/Put. I'm aware that only one side has to be configured for Get/Put. In this case the S71500 will do that (active connection). Do I still need to configure something on the S7400 side? Do I need to configure NetPro to use an unspecified s7 connection? Thx! |
If I could help you, you can use the RATE button. Thank you. |
|
9/29/2016 1:10 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (927) |
Thx guys, It was really easy to setup. On the 400 side, I didn't have to do anything, except the DB must have the same number on both sides. |
If I could help you, you can use the RATE button. Thank you. |
|
10/4/2016 6:42 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (927) |
Yeah correct, The main problem was that they did not set rack+slot of my 400CPU. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
11/18/2016 10:43 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4774 Rating: (123) |
New question published by Damayanti is split to a separate thread with the subject Data exchange between s7-300 PLC and S7-1200 PLC. Best regards |