Hi I have another question regarding S7 communication with Get and Put blocks. I need to set error and status fields and how do I do that? I need this because I want to know when my communication or communication cable is terminated. Pedja ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 12/22/2015 9:20:44 AMNew subject after splitting |
|
12/22/2015 9:53 AM | |
Posts: 1368 Rating:
|
Hello,
each block has an "error" bit and "Status" variable. Both, you can use for detecting error at communication. Look at this faq https://support.industry.siemens.com/cs/de/en/view/82212115 in the first document, you will find also an example for the error handling with PUT/GET (Chapter 3.3/ page 13). Greetings. |
This contribution was helpful to
1 thankful Users |
12/22/2015 4:47 PM | |
Posts: 9 Rating:
|
I´ve menaged to set all parameters correctly and it works fine. Thank You very much for helping, Pedja |