Hello Japi can you please post your 319 related S7 project here for evaluation (and the 315 related project too if you can), this will make it much easier for us to advise on what to check next. For now please check/confirm that you actually used FB14&FB15 GET/PUT (which you must use in a S7-300) rather than SFB14&15 GET/PUT blocks (which you must use in an S7-400). I hope this helps |