Hello, i am working on project, where i need to read data from S7-300 by S7-1200. I can affect only my program in S7-1200. I want to use instruction GET for this task, but i still fails to set connection to this remote PLC. Configuration of connection is in attachment. Outputs of GET function are: NDR = false (never change to true), ERROR = false, Status : 0 Can someone help me where is problem? Base on GET outputs the PLC never try establish connection to partner. Thanks for all advices. Attachmentattachment.zip (99 Downloads) |
11/29/2012 4:32 PM | |
Posts: 126 Rating:
|
Try rack 0, slot 0, connection res of 03. Those are the defaults. |