Hello, if you think that thread is in wrong conference, it is better to use the inform moderators button instead of wrinting it in the post. I now transferred the thread to the conference SIMATIC S7-300 / S7-300F. Best regards O_Moderator |
4/2/2013 3:21 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
You must extend the telegramm to the drive. You must select a address below 64 to be able to use the informations in the PLC part of the T-CPU. In S7T Config (STARTER) you must define in the drive configuration which informations are sended in the additional words of the telegramm extention. You will get the new informations in the selected periphery adresses. Maybe, you will have to change high and low Byte to access the data. Follow this manual, Chapter 5.2.5: http://support.automation.siemens.com/WW/view/en/30119684 te extend the telegramm. In the PDF flile of FAQ 25545745 (http://support.automation.siemens.com/WW/view/en/25545745) you can see how signals of a TB30 are transferred. Due the TB30 informations in this FAQ are used in the technology, a address higher then 64 is used, but you need a address below 64. |