12/15/2018 9:51 AM | |
Joined: 3/17/2014 Last visit: 5/25/2024 Posts: 14 Rating: (0) |
Dear Experts We have a metallizer machine , in this machine in vacuum chamber we have an axis control by a 0.59KW servo and a S110 (6SL3040-0JA01_0AA01) motor module , sometimes it gives us this fault sequence : 30001:power unit over current (fault cause : 11bin ) 7490 : EPOS : Enable signal withdrawn while traversing 30021:Power unit ground fault(0) we changed the power and drive click cable , but after 1 week again the same problem , and this fault always happen in vacuum and when the machine is open we test it a bout 30 time but every thing was right , and I want to know if we have a current leakage from other part of the machine on this motor , can this make the problem for us? with the best wishes
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/17/2018 10:30:11 AMNew subject after splitting |
|
12/16/2018 12:31 PM | |
Joined: 6/28/2017 Last visit: 12/20/2022 Posts: 661 Rating: (40) |
Of course it does ! The F30001 and F30021 fit nicely those circumstances, I believe. Your message isn't clear in terms if it's used a servo motor which was specially designed for vacuum environment and certain vacuum class. Anyway some words on that matter:Electric motors are used in vacuum, they have to be temperature -resistant and largely free of adhesives. So I would say that outgassing might play a nasty joke on the servo motor. Also find in the attachment some more info on that matter. Msorich Attachmentinfluence.pdf (326 Downloads) |