8/6/2020 6:44 AM | |
Joined: 7/1/2016 Last visit: 4/27/2024 Posts: 8 Rating: (0) |
Hi, Good Morning I have S7 1200 1214CDC/DC/DC PLC and 4AI RTD 6ES7 231 5PD32 0XB0. The RTD Module is PT1003Wire so i am getting error high limit exceeded and PLC READ Full values 32676 please help me ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/06/2020 07:55:07New subject after splitting |
|
8/6/2020 10:24 PM | |
Joined: 7/7/2010 Last visit: 5/3/2024 Posts: 14680 Rating: (2350)
|
If jumpers are installed between the 2 analog input terminals for each RTC signal, do they still read 32676? Would you kindly post a screenshot of the hardware configuration, and the schematics for that module showing how the RTDs are wired? It might be a configuration problem. It might be wires in the wrong terminals. It might be the RTDs. Or, the cables, or any connections along the way between the PLC and what the RTDs are sensing.
|
science guy |
|