You can use SFC51 for this. 1) For SF set SSL-ID = W#16#0692 Please check this FAQ. "The status of the DP slave with Address 1 is in Bit 0 of the first byte. If this bit is set, then that DP slave is either defective or disabled. " 2) For BF set SSL-ID = W#16#0292 Please not that these value are valid only if you are using integrated CPU interface. For external DP interface values are W#16#4692 and W#16#4292. For more information you can check the help for sfc51 in your Step 7 installation. |
This contribution was helpful to
1 thankful Users |
6/17/2016 10:38 AM | |
Joined: 8/21/2014 Last visit: 3/24/2023 Posts: 698 Rating:
|
New question published by Akshita Saraswat is split to a separate thread with the subject Getting the ACT LED status. Best regards |