5/26/2014 12:15 PM | |
Joined: 8/27/2010 Last visit: 4/13/2024 Posts: 417 Rating:
Can you please provide more details about hardware configuration you use? |
5/26/2014 1:29 PM | |
Joined: 1/5/2013 Last visit: 11/22/2024 Posts: 283 Rating:
Hello olloy, CPU: 1214c DC/DC/DC with firmware: 3.0 CP: 1242-7 firmware: 1.3.6 the same for both CPUs. |
5/26/2014 2:18 PM | |
Not sure it is a buffer issue. Check the attachment page 38, about triggering the conection establishment. And also, paste here a diagnostics sms content, just to ne sure eveything is ok.
AttachmentBA_CP-1242-7_76.pdf (208 Downloads) |
5/26/2014 3:17 PM | |
Hello olloy, the CPDIAG sms to the passiveCPU: CP 1242-7 V1.3.6 CPU State:RUN GPRS logged in Attach: - NETWORK: provider network name IP: x.x.x.x (Fixed IP with private APN) Signal Quality: good RSSI: 31 i'm talking about the buffer issue (maybe) since if you stop one of the CPUs after the power off-on several times the connection is established automatically within 20-25 seconds but after day or two days i tried to stop the passive CPU the connection is not established again until after 30-45 minutes. |
5/26/2014 3:20 PM | |
Hello SMHZ, Thank you, i'm waiting your details. |
This contribution was helpful to
1 thankful Users |
5/26/2014 3:36 PM | |
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating:
We are planning to use Scalance m874-3 with S7-300. .though havent finalized the solution yet
Follow us on