12/24/2013 1:33 PM | |
Joined: 1/5/2013 Last visit: 11/22/2024 Posts: 283 Rating:
|
Hi, My network topology is attached. Which is better to use Telecontrol mode (with telecontrol basic server) or direct mode? since i don't have the devices yet, i'm in process by purchasing the hardware equipments and the required software. the communication will be ISO on TCP. 1- maximum number of remote stations that be connected to the central PLC using CP1242-7 with a- direct mode b- remote control mode 2- do the direct mode give the GSM signal strenth? Thanks AttachmentSCADA NW Topology v1.2 (SIEMENS Forum).pdf (195 Downloads) |
12/25/2013 11:18 AM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, I understood your drawing like this: You try to collect data in a central PC from remote stations. The central PLC is just used as Gateway between the PC and the remote stations. Correct? Be aware that GPRS (this is the mobile communication supported by the CP1242-7) is limited in bandwidth (typically not more than around 50 kbit/sec in download direction, and less in upload, to be checked with the provider and depending also on the distance to the GSM antenna). The more you will connect remote systems to the central PLC over GPRS, the worse the troughput for each remote system will be. May be you should consider an Internet connection at the central site, wired, + telecontrol server basic. Like depicted here: http://support.automation.siemens.com/WW/view/en/39863979 |
Last edited by: jklm at: 12/25/2013 12:42 PMLast edited by: jklm at: 12/25/2013 11:19 AMBest regards |
|
12/26/2013 6:02 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, For your first suggestion, as told before, I would not use a central PLC, because of the small incoming bandwidth at the central site. But a wired internet connection at the central site instead + telecontrol server basic on the PC (no concentrator PLC at the central site, the remote PLCs send their data directly to the server just like depicted here: http://support.automation.siemens.com/WW/view/en/51065116 For the second suggestion, again, no central S7-1200, because it cannot accept that much connections. But just an OPC server at the central site. As mentionned before you loose the buffering feature in this case. Still based on a central PC (and again without a concentrator PLC), there is a solution based on DNP3, depicted here: http://support.automation.siemens.com/WW/view/en/81162841 These comments are my personal opinion. Ask the sales channel in your country to assist you in defining more in detail what the best alternative is, depending on on your requirements. |
Best regards |
|