Hello PCS7 6.1 sp4 In group display there is a operator request (messageclass 20). When clicked on, it takes me to another screen (in the low hierarchy), but on the page there is no object that needs to be clicked. It doesn't show anymore the purple O sign. The two SFC's in the picture are good, don't need acknowledgement. I checked the top screen for the group display and it is connected to a according to the picture name. Collect value is set at 65535 and YES on the check relevant messages... How can I check where this operator request is coming from?? |
If I could help you, you can use the RATE button. Thank you. |
7/7/2013 5:35 PM | |
Posts: 62 Rating:
Dear Friend, Please Check the in Alarm logging For the source of the Operation Alarm for more Details Please Check the Attached file. Still If it is not Solved Try to run OS Project Editor.this will Resolve the Problem. Regards, Avinash krishna Bhimavarapu