11/5/2008 11:21 AM | |
Posts: 2 Rating:
|
Regards benjas |
4/28/2009 1:56 PM | |
Posts: 8 Rating:
|
Thanks Dchartier.. |
6/11/2009 9:21 AM | |
Joined: 9/27/2006 Last visit: 6/21/2024 Posts: 12260 Rating:
|
Hello senthikumar; From the ABB site, it seems they are using the same RPBA or FBPA adapter from Anybus for their Low voltage AC drives. The specific gsd file you would need is discussed here: ABB Fieldbus Interfaces FAQ: http://library.abb.com/global/scot/scot201.nsf/veritydisplay/ec9a4cdcbd9063bbc125731300423b7b/$File/FAQ_FB_ABB_Drives_20070709.pdf RBPA-01 and FBPA-01 adapters (Profibus) manual and GSD file download: http://www.abb.com/product/seitp322/f12b5520207bb331c1257265002a17d6.aspx In the Fieldbus Options box, select FBPA-Profibus(3) for example.
|
6/11/2009 9:26 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating:
|
Hi senthilkumar, Yes it's possible to create/change gsd file. But I suggest you to try to find necessaries GSD already prepared. · ABB_0812.GSD for PROFIBUS-DPV0 slave mode · ABB10812.GSD for PROFIBUS-DPV1 slave mode (RPBA-01 Rev. H onwards) * * NOTE: If DPV1 mode is used the adapter configuration parameter DP MODE (51.21) should be set to ‘1’. Hope this will helps. Best regards Hristo Mihalev |
Last edited by: UMENCHO at: 6/11/2009 9:27 AMOpps! The next time I''''ll be faster. |
|
10/23/2013 6:44 AM | |
Posts: 1 Rating:
|
thank you |