12/17/2019 9:08 AM | |
Joined: 4/7/2015 Last visit: 11/23/2023 Posts: 27 Rating: (2) |
Hello, experts! We need to full change our hardware from standard type to siplus. Hardware consists from redundancy central racks with CPU-414H, CP-443 and DP racks ET200M with I/O modules. Should we make a change in hardware configuration? Regarding this FAQ it is not required. But there is described regarding only ET200M and S7-300 modules. We didn't find siplus modules in library (Step7 V5.5)
|
Last edited by: Jen_Moderator at: 12/17/2019 13:56:13Optimized link. |
|
12/17/2019 11:27 AM | |
Joined: 9/9/2014 Last visit: 3/26/2024 Posts: 242 Rating: (40) |
Read the topics and FAQ below: Where can you find the manuals and operating instructions for products of the SIPLUS extreme family? It turns out the following situation: Standard devices (PLC or I / O modules or CPs) can be replaced with devices of the "SIPLUS" series without rebuilding the software. This will not require specialized software or any new ones, for example, newest Hardware Support Packages not available in version 5.5 The fact is that devices of the "SIPLUS" series are based on standard versions of devices - see the picture in the attachment (thankdchartier for this) Therefore, you will see in STEP7 standard device - configure and commissioning him, like the device with a standard number (6ES...) |
Last edited by: Jen_Moderator at: 12/17/2019 13:57:10Optimized link. Best Regards |
|