Hi, One of our clients have a S7-400 CPU with Profibus remote racks ET-200s running their process plant. Our hardware configuration has CiR modules configured as per the manual and we have added a couple of I/O modules in the remote racks previously and the hardware update worked with no problems without stopping the CPU (plant continuously running). The problem that we are having now is that we are trying to add a new I/O module in a remote rack DP slave 2 (Profibus Leg 3) but this time we are getting an error and the hardware update fails everytime (attached error screen captures and report below). The error is pointing to DP slave 94 (Profibus Leg 1) which is a slave S7-200 CPU that is working and running. This S7-200 CPU is not the slave where the new module is to be added and it is not located in the same Profibus leg either. Any ideas what could be acusing the problem? Is there any chance that a Profibus communications signal issue with the leg where the S7-200 CPU is connected could be casuing this issue? I would appreciate any comments if you have experienced any similar problems in the past Error Report: ================================ 05/29/2014 2:11:25 PM ================================ Download (13:4793): Error in DP bus modules during CiR Type of error: User data for slave different Log. address of the DP slave: Input address: 94 No relevance to user: (Z3,Byte0) 11 Operating mode: ###FF Priority class: 8 Download (13:4888): No system data was downloaded to the automation system. AttachmentHardware Download Error.zip (55 Downloads) |
6/6/2014 11:50 AM | |
Joined: 10/3/2007 Last visit: 6/2/2023 Posts: 188 Rating:
|
Could it be that the error is not actually pointing to DP slave 94 but to the DP slave witch usesinput address 94? |
Follow us on