Hello Kundrinsss; Have a look at the attached screenshot, taken from the following manual: SIMATIC ET 200M distributed I/O device HART analog modules As you can see, the HART modules must be installed on a deported Profibus-DP rack, and PDM software is needed to calibrate the HART transducers ; to read the data from the HART modules you need to use data record function blocks in the S7 program. Study the manual and come back to us for the next series of questions you will have. Hope this helps, Daniel Chartier |