10/22/2018 12:24 PM | |
Joined: 10/11/2006 Last visit: 4/18/2024 Posts: 5819 Rating: (787)
|
Dear Jeff.kim, 1. booksize ALMs contain the pre-charge device on board. In Chassis-units the pre-charge device is outsourced on AIM. Therefore you don't need a terminal for control signals on booksize. In booksize a line contactor is optional. There is a function module for line contactors implemented. So you can apply a digital output of CU320-2 to control the line contactor. It is closed BEFORE pulses are enabled. You can verify sequence control in LH1: https://support.industry.siemens.com/cs/ww/en/view/109760366 Please note that in case you don't apply a line contactor you always have ~540V DC-link voltage even when switched OFF1. 2. yes, centering is a good idea. And yes, you need to ensure max capacity of DC-link bars of each module in the chain. In your configuration I rather fear you exceed total power capacity of infeed. Nevertheless if you never apply full load on all MoMos simultaneous or just in partial load this configuration should work. |
With best regards, |
|
10/23/2018 4:40 AM | |
Joined: 9/17/2012 Last visit: 4/18/2024 Posts: 81 Rating: (0) |
Hello! Thanks for your kindly reply! It's very helpful to me. Thanks. 감사합니다. |
Wanna improve. |
|