8/7/2017 8:55 PM | |
Posts: 1 Rating: (0) |
I am having problems assigning my F target addresses on a 317F. I am getting a message that says that "The F module is not switching to the required operating mode" when I click on the Identification button (flashing the cards). Any ideas on what could be wrong? I have this problem with multiple cards on several ET200s. ------------------------------------------------------------------------------------------ AttachmentAssign F target address_Failure of Not Switching to Required Operating Mode.jpg (953 Downloads) |
Last edited by: Jen_Moderator at: 8/8/2017 2:23:05 PMNew subject after splitting |
|
This contribution was helpful to1 thankful Users |
9/26/2017 8:30 AM | |
Posts: 1 Rating: (0) |
How did it work out at the end? 'cause i am having the same problem.... no solution found yet :( Thanks |
11/18/2019 3:43 AM | |
Joined: 3/28/2019 Last visit: 8/18/2024 Posts: 3 Rating: (3) |
How's the situation of the topic , I met the same problem on-site |
7/7/2021 11:07 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi together, consider there is a FAQ about this topic. By searching for the error-message you should find it: What should you check when the F destination addresses cannot be assigned?hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to1 thankful Users |