8/16/2009 3:19 PM | |
Joined: 4/6/2006 Last visit: 2/5/2024 Posts: 604 Rating:
|
Hi, Yes this is possible. Just keep the maximum number of connections in mind and this should work without a problem. |
Best regards, |
|
8/16/2009 4:03 PM | |
Joined: 1/7/2006 Last visit: 12/23/2024 Posts: 2705 Rating:
|
Dear Bulmaro. That is no problem, but please consider that the time that is used for the PROFINET IO can't be used for other communication. So please don't switch the PROFINET IO when you don't need it on 1mS update time.... When you have only some PROFINET IO then you don't have to take care at anything. Maybe the switches have to be good ones when you need them the Scalance X200 series is a very good one. |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|