For the you need at least FW V4.6 (https://support.industry.siemens.com/cs/products/6sl3210-1pe23-3ul0). This is why you cannot find it in your catalog, your Scout installation is too old. Two possibilities:
Concerning the error 30711: The new PM has double the rated power. With Safety Integrated activated, the minimal current is monitored (failure message: "Current absolute value too low"). You could try to reduce p9588 to reduce the minimum current required by Safety Integrated. |