3/1/2014 10:48 AM | |
Posts: 8946 Rating:
|
You must ask GE to provide the GSDML file. |
3/2/2014 2:24 AM | |
Joined: 10/7/2005 Last visit: 4/23/2025 Posts: 3047 Rating:
|
Hello alex3429 IBN-Service is correct in case the S7-300 is the Profinet I/O controller and the GE PLC is menat to bethe I/O device. I think though that you want to have it the other way round, correct? If so, you need to create the GSDML file for the S7-300 CPU yourself and import it into GE's Profinet I/O controller configuration program. Have a look at chapter4.8.2 in the SIMATIC PROFINET System Description which contains all the details on how to create aGSDML file for anS7-300 CPU (aka I-Device). I hope this helps. |
Cheers |
|
This contribution was helpful to
2 thankful Users |
3/4/2014 4:15 PM | |
Posts: 2 Rating:
|
Thank you fritz, GSDML file created. Regards. alex3429
|
This contribution was helpful to
2 thankful Users |
3/31/2015 4:55 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating:
|
|
2/8/2017 11:47 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating:
|
New question published by lorenzo.gepponi is split to a separate thread with the subject RX3i GE plc used like Controller and a S7-300 used like i-device. Best regards |