11/24/2016 10:21 AM | |
Posts: 2 Rating:
|
Thank you so much. I tested it here and it worked. I assign the value to the first scan.
|
2/15/2017 9:06 PM | |
Joined: 9/25/2012 Last visit: 3/14/2025 Posts: 10 Rating:
|
Hello I have the same setup and problem. I try this solution but no connection. The Busy output of the master block stays True. I use Modbus RTU V3.0 on the CPU 1512 V2.0 and has done the Firmware upate 6ES7512-1DK01-0AB0_V205. Connection on CP RS485 terminal 12 and 14. I am sure that the slave is working and is available because I can make a working connection between the Slave and a S7-1212 PLC. Modbus adres 10. Please Help. AttachmentModbus.pdf (975 Downloads) |
9/15/2019 3:00 PM | |
Joined: 12/27/2014 Last visit: 3/14/2025 Posts: 4 Rating:
|
For Using ET200SP Module 6ES7 137-6AA00-0BA0 in RS485-2 wire mode. Declare in the Interface of the hardware properties for CM_ptp Points to be taken care of are 1. Terminals to be used for wiring are 12 and 14. 2. In first network move 4 to "Modbus_Comm_Load_DB"s "MODE" parameter. Ucan Use first scan or direct move option to move value. 3. After moving the value then only call the "Modbus_Comm_Load" block. with the first scan at REQ 4. Then call Modbus Master or Modbus Slave Block. AttachmentMODBUS RTU CM_PTP 137-6AA00-0BA0.docx (1247 Downloads) |
This contribution was helpful to
1 thankful Users |