7/22/2010 3:28 PM | |
Posts: 5822 Rating:
|
Hello,
|
7/23/2010 1:08 AM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello Peter; Are you addressing the slave while it isa connected to the As-i bus? It is always recommended to address a slave while it is removed from the bus, ensuring that there are no conflictswith existing slaveaddresses; this is particularily true for new, out-of-the-box slave units, that all have the same address (factory-installed). Only if each slave is attributed a unique address can the As-i bus startup. From the As-i manual recommended by J_Bell earlier: Addressing the slaves You can set the slave address in different ways: ● Offline with the addressing unit via the addressing socket or at the AS-i connection. Recommended when assigning addresses for the entire system. The direct connection between the slave and addressing unit ensures that the slave modules are not mixed up. ● Online by the AS-i master and in the PLC configuration software. Recommended for assigning addresses to individual slaves if an addressing unit is not available. Before assigning addresses, you must ensure that each address exists onlyonce in the AS-i network, that is, several new, additional modules (with address 0 in as-delivered condition) must not be connected to the AS-i cable. If two or more modules with the same slave address are detected at the AS-i bus, dbladd is displayed at the instrument. The corresponding address blinks in the address field. |
Last edited by: dchartier at: 7/23/2010 1:09 AM |
|